With a security module, how to use a Double EOL resistor zone ?
I want to use a double EOL resistor zone. The PIR connected to this zone is OK, I get on it:
5,6 kOhms when no motion is detected
11,2 kOhms when motion is detected
open circuit when tamper is activated (PIR box opened)
In device manager, zone wiring is defined as "Double EOL resistor zone"
In device browser, I made a partition using this zone with type "Perimeter". When the partition is armed, motion detection works and siren is activated but tamper activation (by opening the PIR without detecting motion) doesn't trigger alarm.
I tried to add a second zone in the partition using the same physical zone with type "Tamper". With new interface, this is not possible, I get a "Duplicate UUID" message. With old interface, I can add this second zone, then I can see events on it but alarm is not triggered by these events.
Thank you for help.
I answer myself: in new interface there is a configure button allowing to define how tamper zones works. Old interface doesn't have it. It's a pity that some functions are only in old interface and some others are only in new interface :-(
I answer myself: in new interface there is a configure button allowing to define how tamper zones works. Old interface doesn't have it. It's a pity that some functions are only in old interface and some others are only in new interface :-(