Flush On/Off thermostat - Qubino
Under Consideration
hello,
can anyone help me please with my thermostat topic. Something is totally in the opposite way.
Heater: 230V/600Watt Infrared heater
Thermostat: Qubino Flush On/Off thermostat (ZMNHIA2)
Scenario1
Room: 20.3°C
Setpoint: 25.0°C
-> Heater switched OFF (0.0Watt and no 0V outlet measured)
Szenario2
Room: 20.3°C
Setpoint: 11.0°C
-> Heater switched ON (613,5 Watt and 230V outlet measured)
Thanks for your help.
Greets
You can't vote. Please authorize!
You can't vote. Please authorize!
You can't vote. Please authorize!
No connection
Real-time notifications may not work


I like this idea
I had same problem. Change relay switch selection to NC (Normaly Close). There are a problem with hysteresis on and off. It should be
0-127 = 0 - 12,7°C it´s ok in zipabox
128-255 = -0,1 - -12,7°C but in zipabox it is 128 = -12,8°C and 255 = -1°C
For me it works with settings in picture.
I had same problem. Change relay switch selection to NC (Normaly Close). There are a problem with hysteresis on and off. It should be
0-127 = 0 - 12,7°C it´s ok in zipabox
128-255 = -0,1 - -12,7°C but in zipabox it is 128 = -12,8°C and 255 = -1°C
For me it works with settings in picture.